If this is your first visit, be sure to
check out the FAQ by clicking the
link above. You may have to register
before you can post: click the register link above to proceed. To start viewing messages,
select the forum that you want to visit from the selection below.
Part of the 'SELF HELP WITH MORE' group of
websites {click on the menu link above}.
a client want's me to install a wall and door to close in her furnace room, it currently has 3 walls .
i was wondering if there was a code for some kind of vent on the door or could i get away with a louver door?
Where does the furnace get it's combustion air? Is there an outside air intake?
Check the furnace's install manual for minimum clearances before you close it off. It will also tell you how big of vents (usually 2) that are needed in the door if it takes air from the room. If it's a sealed combustion chamber there may still be a requirement for airflow into the room.
Also, since you are making a furnace room, you need lighting and a service outlet in the room. Make sure there is room to work on the furnace, remove all the covers and to replace the furnace when it comes time.
yes outside air, it's a high efficiency furnace. there is a recepticle and lighting and room to work on the furnace. wouldn't a full louver door be enough venting?
We process personal data about users of our site, through the use of cookies and other technologies, to deliver our services, personalize advertising, and to analyze site activity. We may share certain information about our users with our advertising and analytics partners. For additional details, refer to our Privacy Policy.
By clicking "I AGREE" below, you agree to our Privacy Policy and our personal data processing and cookie practices as described therein. You also acknowledge that this forum may be hosted outside your country and you consent to the collection, storage, and processing of your data in the country where this forum is hosted.
Comment