posted by: hawkertech
I have a newer 100A service panel and am planing on running 6/3 copper about 60 feet to a small sub panel in my attached garage to add circuits there so I don't have to make several long 12/2, 10/2 runs to add what I want there. Yes I know most service panels are installed in the garage but mine is in the basement at the other end of the house which was built in 62. I plan on feeding it with a double 50A breaker but I have heard from some people on other forums that I can feed it with a 60A breaker. This does not seem right to me since 6awg is rated for 55A. Am I correct is saying that you can not use a double 60A breaker on 6/3 wire for 220V?
I have a newer 100A service panel and am planing on running 6/3 copper about 60 feet to a small sub panel in my attached garage to add circuits there so I don't have to make several long 12/2, 10/2 runs to add what I want there. Yes I know most service panels are installed in the garage but mine is in the basement at the other end of the house which was built in 62. I plan on feeding it with a double 50A breaker but I have heard from some people on other forums that I can feed it with a 60A breaker. This does not seem right to me since 6awg is rated for 55A. Am I correct is saying that you can not use a double 60A breaker on 6/3 wire for 220V?