posted by: dkerr
I received this by email, have sent a reply with the link to this thread....
I have a situation where a new gfci breaker was installed and then armoured cable was run to a junction box to connect with the original ungrounded wires. The ground was cut short as per Rule 26-700 which allows it -- As an alternative to bonding the Code also states "grounding type receptacles without a bonding conductor shall be permitted to be installed provided each receptacle is protected by a ground fault circuit interrupter of the Class A type that is an integral part of this receptacle; or supplied from a receptacle containing a ground fault circuit interrupter of the Class A type; or supplied from a circuit protected by a ground fault circuit interrupter of the Class A type. Where this option is used, no bonding conductor is permitted between outlets unless that bond conductor is in turn connected to ground.
When I connect the wires, the ground on the 14-2 wire becomes hot/live, even though the ground isn't connected to anything.
Can I connect the ground of the armoured cable to the junction box and then connect the ground of the 14-2 wire to a pigtail running off the j-box? The 14-2 wire would then be grounded at our bathroom receptacle and vanity light switch box. This path would then be continuously grounded back to the panel. The question is made complicated because there is also an additional branch that is coming from the same junction box which is 2-wire with the black and whites connected with the other wires, but which obviously doesn't have a ground.
Is this to Ontario code since one branch has a continuous path to ground, while the second branch does not?
The second alternative is to jut cut the ground wire short on either end of the 14-2 cable and just leave it in the j-box, even though it is hot/live. My concern here is what if the outer insulation in the wire is nicked at some point and thereby exposes the live bare ground wire which could potentially star a fire.
I received this by email, have sent a reply with the link to this thread....
I have a situation where a new gfci breaker was installed and then armoured cable was run to a junction box to connect with the original ungrounded wires. The ground was cut short as per Rule 26-700 which allows it -- As an alternative to bonding the Code also states "grounding type receptacles without a bonding conductor shall be permitted to be installed provided each receptacle is protected by a ground fault circuit interrupter of the Class A type that is an integral part of this receptacle; or supplied from a receptacle containing a ground fault circuit interrupter of the Class A type; or supplied from a circuit protected by a ground fault circuit interrupter of the Class A type. Where this option is used, no bonding conductor is permitted between outlets unless that bond conductor is in turn connected to ground.
When I connect the wires, the ground on the 14-2 wire becomes hot/live, even though the ground isn't connected to anything.
Can I connect the ground of the armoured cable to the junction box and then connect the ground of the 14-2 wire to a pigtail running off the j-box? The 14-2 wire would then be grounded at our bathroom receptacle and vanity light switch box. This path would then be continuously grounded back to the panel. The question is made complicated because there is also an additional branch that is coming from the same junction box which is 2-wire with the black and whites connected with the other wires, but which obviously doesn't have a ground.
Is this to Ontario code since one branch has a continuous path to ground, while the second branch does not?
The second alternative is to jut cut the ground wire short on either end of the 14-2 cable and just leave it in the j-box, even though it is hot/live. My concern here is what if the outer insulation in the wire is nicked at some point and thereby exposes the live bare ground wire which could potentially star a fire.