posted by: Ephemeral_Glow
I knocked out the wall between my office and the kitchen upstairs so that the combined space will be all kitchen with room for two freezers so there will be no more running to he garage for meat n' bread. The downstairs kitchen then becomes a bar / art studio functionally. I'm installing a subpanel upstairs, in the middle of the house, and then another subpanel in the garage.
I read at
WEB LINK
If there are permanent provisions for food prep and cooking appliances AND a sink, then it's still considered a kitchen.
Q1: Would I be able to argue that the gas stove in the lower kitchen will remain for candlemaking/commercial purposes ? Does a lack of food make it no longer a cooking appliance ? If I were to move the stove to the garage and have a sink in the garage, does my garage then become a kitchen ?
I should mention that the house has some older cloth-covered romex type NM that is green, which has a reduced ground size. I have read that a full-sized ground has been required since ~1972, although, I am used to seeing a reduced ground on all wiring of larger scale, so I'm skeptical about that requirement.
Q2: True ? If so, does it only apply to "small conductors" ?
Q3: What is the rating of this NM cable and what are the conductors rated for seperately ? Many of these wires run through the attic. Do I use the 60 degree column of 310.16 and apply the correction factor from the 60 degree column as well or do I get to use a higher column for applying correction factors ?
Q4: I understand that modifying or extending a circuit requires upgrading to code. If I were to take the home-run for a circuit out of the main panel and run it to the nearer and newer subpanel, would this still be considered a modification ? I know extending under 6 ft is not a problem but is cutting back the home run ?
At a later time, I plan on adding additional lighting to every room in the house. The builders thought one overhead light in the middle of a room was adequate, hence, I find I am always working in my shadow, especially at the lower kitchen counters since there is no under cab lighting.
Q5: The refridgeration circuit I have planned has three appliances: 3A, 6A, and 7.8A , for a total of 16.8 Amps. Times that by a 1.75 for heat pump / compressor motor loading, that comes to 29.4A. I would put it all on one circuit but the plugs on the appliances are for normal 15-20A receptacles. I was thinking of putting them [(3A + 6A) and (7.8A)]on a multiwire circuit since I have some 12/3-w/grd cable. Or seperately. I would have to derate the wire for ambient temp in the attic which I figure is ~125-130 degree F . What do you think would be the cheapest or best way of wiring for this?
Q 6-7-8: I will be putting in 12 volt tape light all over in the kitchen and the tape light itself is fairly cheap but the little transformers are going to kill me at about $40 a pop. Instead of buying 10 of these, I have an old battery charger that's mid-size, probably 20 or 30 Amp. Haven't quite figured out yet, but it's heavy. I would like to cut the clamps off of the leads and put plugs on them, feed power to the charger from a Rx, break the tab on the Rx, and feed power backing into the rest of the switched and dimmed circuit and effectively power the rest of the Rx's that will power the individual tape lights. The kitchen tape lighting would only take ~5A and I would like to use the extra capacity to power tape lights in closets throughout the house. Effectively, I'd be making my own 12 volt lighting circuit. I would stash the charger in a kitchen cabinet so it might have to be derated for being in an enclosed space as well. A couple of other questions arise out of this idea. What are battery chargers or transformer's rated for with continous usage ? The normal 80% ? Also, would I need to have a special receptacle and plugs so that no one ever tries to plug a 120 volt appliance into the 12 volt circuit or would labeling suffice ?
Q9-10: I'm installing two garbage disposals under two single 25x22 side-by-side undermount sinks. They are 6A and 8A and I figure that multiplied by 1.75 for motor loads is 10.5A and 14A. Should I put two motors on a multi-wired receptacle ? I hear people say that multiwire's are bad practice because if the neutral is broken, the circuit is still live. I could see that, with higher voltage at some of the appliances or devices on the side that is less loaded and lower voltage on side that is more loaded. I wouldn't want to fry appliances or bulbs later on from a loose neutral. I say that if the loads are perfectly balanced it won't, but what will happen if the neutral is broken and there is an amp or two difference between the loads ?
My father-in-law is a industrial electrician and we went over my calculations about the cable I need for the sub-panels and we disagree on wire sizes. I need someone to tell me whether I'm right or whether I have my head cross-threaded on my neck.
I'm inclined to buy from Menards and they sell only two sizes of SER cable, 2-2-2-4 AL and 4/0-4/0-4/0-2/0 AL. SE-R is basically like Romex and there are new rules that allow me to use the 310.16 table for branch circuits since the subpanels do not supply the whole load of a family dwelling.
My calculation goes like this: The old NEC Table 310.16 shows an ampacity of 100 in the 90 degree column for the 2-2-2-4 AL SE-R cable. I use the 90 degree column because the subpanel feeder goes through the attic for most of the run and attic temp around here can go as high as 125-130 degrees in summer, so I apply a correction factor of 76%. So, 100 x .76 = 76 Amps . The feeder is also going to run from the main in the basement, up through an outside wall that has thermal insulation, so I'm required not to exceed the 60 degree ampacity after correction factors are applied. The 60 degree ampacity is 75 Amps, so very close to the 76 after corrections using the 90 degree ampacity. Being that these subpanels will have two hot legs, to me, that means each leg can carry 75 Amps for a combined 150 Amps of power. I'm plenty happy with that, since the worst case demand would be 144 Amps with all the future additions and a full house of kids that leave all the lights on like my brother did growing up... Is this calculation right, or should I get the 4/0 like my father-in-law says because... Table 310.16 actually refers to the ampacity of two conductors ?
My main requires a QO-C style 4 space breaker for a 150-200A branch. Personally, I would want a 4 space for anything 100A or more. If there was a 6 space 150A breaker I'd buy it. The main sticker states that a 2 space breaker is okay for 125A. Yeah right. Personally, I think big breakers are okay for motor start-ups, but I don't trust those blades to carry continuous power. Am I just paranoid or a little OCD ? Anyone know of a big box store that carries 4 space QO-C breakers ? I've got an electrical supply place picked out otherwise.
I have inherited a box of spare breakers that I intended to use in the new subpanels of the same style. With the new Arc fault requirements on everything 20A and under, many of the breakers I have now are going to be useless except I read that commercial electric is exempt from the arch-fault requirement. Being that I will be starting a business in my garage, would I be able to use up some of these plain breakers in conjunction with GFCI receptacles to wire up the new circuits ?
I believe the difference between calculations stems from my belief that Table 310.16 refers to the ampacity of a single conductor, and not two as my father-in-law believes. I say that the ampacity listed is for the conductance of voltage to the neutral point, where the neutral wire is not a 2nd conductor, but merely an extension of the first conductor to the neutral point back at the neutral bus bar. Each leg of a two leg subpanel conducts to the neutral point at it's neutral bus bar and the neutral grounded conductor only carries the minor imbalance between the bus bars. True ?
In an imperfect world, with a sub-panel imperfectly balanced due to difference in breaker numbers, I'm bound to have a load that is 5, 10, 15, worst case 20 Amps out of balance between the two legs. I could figure on having the legs at max 20 amps out of balance, so I could safely expect one leg to carry 75 and the other 55, for a combined 130 Amps total load. So then I should only put a 125 breaker in the main feeding a 125 Amp subpanel instead of a 150A breaker and subpanel ?
I know that sounds like a lot of power and I probably could run the whole house off of that. One of the items in my load calculation that I think is off is for the electric range. It has a 50A plug on it. I know it will never draw that. I assume that the name-plate rating is for all four burners on and the oven on high. Typical use would be one or two burners being turned on at a time with the oven. I know I can apply an 80% demand factor on an electric range, but that seems to get canceled out by the 125% loading factor typical of 240V heating units. I feel that 50A is really at least 10A overboard, and I don't really believe I would need 144A of peak power. But on the otherhand, I'd feel like an idiot for putting a 125A panel on a feeder that is actually rated for 150A cable that I paid good money for.
Extra credit, why is the neutral tied to the wider blade of a plug ? It has to be one way or the other. Is it because if an applaince receives current from outside of it's supply current, it will be able to handle the load and the short ? Or is it because if there is a short from the supply side, we would prefer the smaller blade to burn out first ?
Not really important, just thought I'd throw it out there while I'm asking a million questions...
I knocked out the wall between my office and the kitchen upstairs so that the combined space will be all kitchen with room for two freezers so there will be no more running to he garage for meat n' bread. The downstairs kitchen then becomes a bar / art studio functionally. I'm installing a subpanel upstairs, in the middle of the house, and then another subpanel in the garage.
I read at
WEB LINK
If there are permanent provisions for food prep and cooking appliances AND a sink, then it's still considered a kitchen.
Q1: Would I be able to argue that the gas stove in the lower kitchen will remain for candlemaking/commercial purposes ? Does a lack of food make it no longer a cooking appliance ? If I were to move the stove to the garage and have a sink in the garage, does my garage then become a kitchen ?
I should mention that the house has some older cloth-covered romex type NM that is green, which has a reduced ground size. I have read that a full-sized ground has been required since ~1972, although, I am used to seeing a reduced ground on all wiring of larger scale, so I'm skeptical about that requirement.
Q2: True ? If so, does it only apply to "small conductors" ?
Q3: What is the rating of this NM cable and what are the conductors rated for seperately ? Many of these wires run through the attic. Do I use the 60 degree column of 310.16 and apply the correction factor from the 60 degree column as well or do I get to use a higher column for applying correction factors ?
Q4: I understand that modifying or extending a circuit requires upgrading to code. If I were to take the home-run for a circuit out of the main panel and run it to the nearer and newer subpanel, would this still be considered a modification ? I know extending under 6 ft is not a problem but is cutting back the home run ?
At a later time, I plan on adding additional lighting to every room in the house. The builders thought one overhead light in the middle of a room was adequate, hence, I find I am always working in my shadow, especially at the lower kitchen counters since there is no under cab lighting.
Q5: The refridgeration circuit I have planned has three appliances: 3A, 6A, and 7.8A , for a total of 16.8 Amps. Times that by a 1.75 for heat pump / compressor motor loading, that comes to 29.4A. I would put it all on one circuit but the plugs on the appliances are for normal 15-20A receptacles. I was thinking of putting them [(3A + 6A) and (7.8A)]on a multiwire circuit since I have some 12/3-w/grd cable. Or seperately. I would have to derate the wire for ambient temp in the attic which I figure is ~125-130 degree F . What do you think would be the cheapest or best way of wiring for this?
Q 6-7-8: I will be putting in 12 volt tape light all over in the kitchen and the tape light itself is fairly cheap but the little transformers are going to kill me at about $40 a pop. Instead of buying 10 of these, I have an old battery charger that's mid-size, probably 20 or 30 Amp. Haven't quite figured out yet, but it's heavy. I would like to cut the clamps off of the leads and put plugs on them, feed power to the charger from a Rx, break the tab on the Rx, and feed power backing into the rest of the switched and dimmed circuit and effectively power the rest of the Rx's that will power the individual tape lights. The kitchen tape lighting would only take ~5A and I would like to use the extra capacity to power tape lights in closets throughout the house. Effectively, I'd be making my own 12 volt lighting circuit. I would stash the charger in a kitchen cabinet so it might have to be derated for being in an enclosed space as well. A couple of other questions arise out of this idea. What are battery chargers or transformer's rated for with continous usage ? The normal 80% ? Also, would I need to have a special receptacle and plugs so that no one ever tries to plug a 120 volt appliance into the 12 volt circuit or would labeling suffice ?
Q9-10: I'm installing two garbage disposals under two single 25x22 side-by-side undermount sinks. They are 6A and 8A and I figure that multiplied by 1.75 for motor loads is 10.5A and 14A. Should I put two motors on a multi-wired receptacle ? I hear people say that multiwire's are bad practice because if the neutral is broken, the circuit is still live. I could see that, with higher voltage at some of the appliances or devices on the side that is less loaded and lower voltage on side that is more loaded. I wouldn't want to fry appliances or bulbs later on from a loose neutral. I say that if the loads are perfectly balanced it won't, but what will happen if the neutral is broken and there is an amp or two difference between the loads ?
My father-in-law is a industrial electrician and we went over my calculations about the cable I need for the sub-panels and we disagree on wire sizes. I need someone to tell me whether I'm right or whether I have my head cross-threaded on my neck.
I'm inclined to buy from Menards and they sell only two sizes of SER cable, 2-2-2-4 AL and 4/0-4/0-4/0-2/0 AL. SE-R is basically like Romex and there are new rules that allow me to use the 310.16 table for branch circuits since the subpanels do not supply the whole load of a family dwelling.
My calculation goes like this: The old NEC Table 310.16 shows an ampacity of 100 in the 90 degree column for the 2-2-2-4 AL SE-R cable. I use the 90 degree column because the subpanel feeder goes through the attic for most of the run and attic temp around here can go as high as 125-130 degrees in summer, so I apply a correction factor of 76%. So, 100 x .76 = 76 Amps . The feeder is also going to run from the main in the basement, up through an outside wall that has thermal insulation, so I'm required not to exceed the 60 degree ampacity after correction factors are applied. The 60 degree ampacity is 75 Amps, so very close to the 76 after corrections using the 90 degree ampacity. Being that these subpanels will have two hot legs, to me, that means each leg can carry 75 Amps for a combined 150 Amps of power. I'm plenty happy with that, since the worst case demand would be 144 Amps with all the future additions and a full house of kids that leave all the lights on like my brother did growing up... Is this calculation right, or should I get the 4/0 like my father-in-law says because... Table 310.16 actually refers to the ampacity of two conductors ?
My main requires a QO-C style 4 space breaker for a 150-200A branch. Personally, I would want a 4 space for anything 100A or more. If there was a 6 space 150A breaker I'd buy it. The main sticker states that a 2 space breaker is okay for 125A. Yeah right. Personally, I think big breakers are okay for motor start-ups, but I don't trust those blades to carry continuous power. Am I just paranoid or a little OCD ? Anyone know of a big box store that carries 4 space QO-C breakers ? I've got an electrical supply place picked out otherwise.
I have inherited a box of spare breakers that I intended to use in the new subpanels of the same style. With the new Arc fault requirements on everything 20A and under, many of the breakers I have now are going to be useless except I read that commercial electric is exempt from the arch-fault requirement. Being that I will be starting a business in my garage, would I be able to use up some of these plain breakers in conjunction with GFCI receptacles to wire up the new circuits ?
I believe the difference between calculations stems from my belief that Table 310.16 refers to the ampacity of a single conductor, and not two as my father-in-law believes. I say that the ampacity listed is for the conductance of voltage to the neutral point, where the neutral wire is not a 2nd conductor, but merely an extension of the first conductor to the neutral point back at the neutral bus bar. Each leg of a two leg subpanel conducts to the neutral point at it's neutral bus bar and the neutral grounded conductor only carries the minor imbalance between the bus bars. True ?
In an imperfect world, with a sub-panel imperfectly balanced due to difference in breaker numbers, I'm bound to have a load that is 5, 10, 15, worst case 20 Amps out of balance between the two legs. I could figure on having the legs at max 20 amps out of balance, so I could safely expect one leg to carry 75 and the other 55, for a combined 130 Amps total load. So then I should only put a 125 breaker in the main feeding a 125 Amp subpanel instead of a 150A breaker and subpanel ?
I know that sounds like a lot of power and I probably could run the whole house off of that. One of the items in my load calculation that I think is off is for the electric range. It has a 50A plug on it. I know it will never draw that. I assume that the name-plate rating is for all four burners on and the oven on high. Typical use would be one or two burners being turned on at a time with the oven. I know I can apply an 80% demand factor on an electric range, but that seems to get canceled out by the 125% loading factor typical of 240V heating units. I feel that 50A is really at least 10A overboard, and I don't really believe I would need 144A of peak power. But on the otherhand, I'd feel like an idiot for putting a 125A panel on a feeder that is actually rated for 150A cable that I paid good money for.
Extra credit, why is the neutral tied to the wider blade of a plug ? It has to be one way or the other. Is it because if an applaince receives current from outside of it's supply current, it will be able to handle the load and the short ? Or is it because if there is a short from the supply side, we would prefer the smaller blade to burn out first ?
Not really important, just thought I'd throw it out there while I'm asking a million questions...