Wiring Done Right

Collapse

Announcement

Collapse
No announcement yet.

SE Cable

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • SE Cable

    Posted By: ohm1more

    Can #8 Alum SE cable be fused at 40 amps?

  • #2
    Posted By: suemarkp

    If it is one of those cases where you can fuse higher than ampacity (welders, motors, HVAC), then yes. Otherwise, you're stuck at the 30A ampacity rating if you're under the 2008 or later code.

    Comment


    • #3
      Posted By: ohm1more

      For some reason, I thought I put the year (2005) down….HUM!!
      And no it has nothing to do with welders etc. It’s a typical branch circuit serving a cooking appliance.

      Comment

      Working...